Default Ducted gas heating problem

Hi from my freezing home.
My ducted gas heat heater has been working fine up until yesterday I went to investigate before calling someone who will come and charge me a fortune. What I found was it all works as it should if the steel cover over the fan box is removed but once I put it back on while running there is a lot of suction and the fan stops blowing? What could cause this or should I listen to the wife and call someone?

Thanks
Tregs
__________________
Missing the turbo feeling can’t wait to get back into another xr6t
tregs is offline   Reply With Quote Multi-Quote with this Post
Old 07-11-2016, 02:52 PM   #2
bingoTE50
Steve
 
bingoTE50's Avatar
 
Join Date: Jun 2007
Location: Sth East Qld
Posts: 1,284
Default Re: Ducted gas heating problem

Could be a capacitor on a the fan motor or the motor itself . Sounds like if you don't relieve the pressure it stalls . The motor may have a internal overload as well ? All I can think of . I am no expert by the way !
__________________
Currently no Fords . 2005 Statesman International 5.7, Mazda 2 and a Hilux.
Former Fords: 2010 Ford Escape 2007 BF11 GT, TE50 Series 1 ,AU V8 One Tonner ,EL Falcon Wagon, ED Fairmont , EB Falcon Series 1. Mk 2 Cortina
Company Fords : 3 BA Falcons , EB 11 Falcon Wagon , Ford F350 351 V8.
bingoTE50 is offline   Reply With Quote Multi-Quote with this Post
Old 07-11-2016, 03:12 PM   #3
FoxtrotGolfXray 5.0
Donating Member
Donating Member3
 
FoxtrotGolfXray 5.0's Avatar
 
Join Date: Mar 2007
Location: Heading thru Hell (Corner)
Posts: 8,054
Technical Contributor: For members who share their technical expertise. - Issue reason: Willingly providing technical info and documents, despite glitches. 
Default Re: Ducted gas heating problem

My advice is to listen to the wife and call in someone who knows what they are talking about.

There are so many things that can go wrong with a gas system, so don't muck around with it. Paying to get it fixed correctly is cheaper than potentially harming yourself and your loved ones.
__________________
Labels are for jars, not for people.

Life is a journey, not a destination.

~~~~~~~~~~~~~~

Daily: 2013 FGII EcoLPi in Winter White
Play: 2015 FG X XR8 in Emperor Show' N Shine thread

Gone, but not forgotten: 2015 SZII petrol Titanium Territory in Emperor
FoxtrotGolfXray 5.0 is offline   Reply With Quote Multi-Quote with this Post
Old 07-11-2016, 04:10 PM   #4
olfella
Cranky old bastard
 
Join Date: Dec 2004
Posts: 9,393
Default Re: Ducted gas heating problem

Have you tried cleaning/removing the inside return air filter? It may be clogged up.
__________________
"But really...what can possibly go wrong"
olfella is offline   Reply With Quote Multi-Quote with this Post
Old 07-11-2016, 04:40 PM   #5
GO FURTHER
Moderator
Donating Member3
 
GO FURTHER's Avatar
 
Join Date: Jan 2014
Location: Melbourne
Posts: 7,940
Tech Writer: Recognition for the technical writers of AFF - Issue reason: Fitting New Iridium Plugs & the state of the old ones - (Photo Essay) 
Default Re: Ducted gas heating problem

Sounds like you have a blocked air filter in the return air grille.
When was the last time you took it out and vacuumed or washed it?
It should be done at least every couple of months, especially in winter.
GO FURTHER is offline   Reply With Quote Multi-Quote with this Post
Old 07-11-2016, 04:57 PM   #6
pursuit57
mortgage free !
 
Join Date: May 2012
Location: Lower Mid Nth Coast NSW
Posts: 496
Default Re: Ducted gas heating problem

There is SO MANY things that can be at fault - simple or complex.
As previously said by a member, first check your return air filter.
You have been doing this regularly before - right ?

As a retired sparky & a/c tech, it amazed me amount of times filters were blocked solid - owners said " I didn't know that was there or had to be cleaned "

Otherwise there are many controls & safety devices which you cannot touch or adjust by law so get a professional in...
Example : one of the potential faults is the airflow safety switch or oxygen depletion safety, which prevents the gas ignition when low air flow (or no minimum outside air is present) this may be doing it's job if your filters need cleaning or a damper is closed or other failure.
With you opening the cover you are allowing air to bypass air flow switch etc, etc.

But for safety sake if filter cleaning doesn't fix call in a pro to check whole system out - especially if you bought the place after it was fitted
__________________
My previous Ford's : FG MKII XR6 - AUIIXR6 Ute - EA Ghia - XD 351 - XC Coupe 351 - XB Fairmont 302 - XYGT 351 - XW 302
pursuit57 is offline   Reply With Quote Multi-Quote with this Post
2 users like this post:
Old 07-11-2016, 09:00 PM   #7
ford71V8
FF.Com.Au Hardcore
 
ford71V8's Avatar
 
Join Date: Mar 2012
Posts: 4,841
Default Re: Ducted gas heating problem

My only advice would be to make sure nobody from Mannix or Climat enter your home and mess with your heating.

Never dealt with a more hopeless bunch.
By the time they got my system installed and running correctly, winter was almost over.
ford71V8 is offline   Reply With Quote Multi-Quote with this Post
Old 08-11-2016, 12:14 AM   #8
tregs
FF.Com.Au Hardcore
 
tregs's Avatar
 
Join Date: Sep 2007
Posts: 698
Default Re: Ducted gas heating problem

Thanks for all the replies I ended up calling someone out to have a look. The problem is was the inlet duct had come lose and every time it tried to suck air it would suck itself closed. I'm kicking myself for not checking or thinking about checking that. But in the end I'm relieved that it was an easy fix all up he was here for 45 minutes.
__________________
Missing the turbo feeling can’t wait to get back into another xr6t
tregs is offline   Reply With Quote Multi-Quote with this Post
3 users like this post:
Old 08-11-2016, 01:12 AM   #9
xr8cam
Guest
 
Join Date: Feb 2012
Location: Sydney
Posts: 653
Default Re: Ducted gas heating problem

Quote:
Originally Posted by bingoTE50 View Post
Could be a capacitor on a the fan motor or the motor itself . Sounds like if you don't relieve the pressure it stalls . The motor may have a internal overload as well ? All I can think of . I am no expert by the way !
Any idea where I can buy the capacitors needed for a split system? I see e online for $8 and they look the same as the ones I get charged hundreds for by aircon techs.
xr8cam is offline   Reply With Quote Multi-Quote with this Post
Old 08-11-2016, 12:24 PM   #10
GO FURTHER
Moderator
Donating Member3
 
GO FURTHER's Avatar
 
Join Date: Jan 2014
Location: Melbourne
Posts: 7,940
Tech Writer: Recognition for the technical writers of AFF - Issue reason: Fitting New Iridium Plugs & the state of the old ones - (Photo Essay) 
Default Re: Ducted gas heating problem

Quote:
Originally Posted by xr8cam View Post
Any idea where I can buy the capacitors needed for a split system? I see e online for $8 and they look the same as the ones I get charged hundreds for by aircon techs.
Try Actrol Refrigeration stores or Middys.... Both have branches nationally.
You will need to know the size, better still, take the old one in with you.
GO FURTHER is offline   Reply With Quote Multi-Quote with this Post